Electrical wire crossing cold air return duct

Ask your electrical related questions here
Post Reply
rao.manoj2004
Posts: 19
Joined: Mon Oct 22, 2018 3:29 pm

Electrical wire crossing cold air return duct

Post by rao.manoj2004 » Mon Oct 22, 2018 3:33 pm

Untitled.png
Untitled.png (871.77 KiB) Viewed 196 times
Hi... I am running wire for electrical outlets (finishing basement) in walls and have two cold air return duct in walls (between 2 studs) ... can I pass electrical wire through these cold air return as per ontario electrical code? Thanks in advance for help :)


User avatar
emtnut
Posts: 1491
Joined: Mon Mar 02, 2015 7:21 am
Location: Canada
Contact:

Re: Electrical wire crossing cold air return duct

Post by emtnut » Mon Oct 22, 2018 4:17 pm

Yes, you can pass perpendicular through the cold air duct (as you did)

You cannot run parallel (lengthwise) in the duct (ie using the duct as a conduit)
~~ This space for rent ... apply within :mrgreen: ~~

User avatar
Shannon
Posts: 11413
Joined: Fri Nov 25, 2011 11:58 pm
Location: Canada
Contact:

Re: Electrical wire crossing cold air return duct

Post by Shannon » Mon Oct 22, 2018 5:07 pm

I would recommend you seal up the holes after all the wires are run. Caulking or spray foam would be fine.
If you've found our videos or website information helpful, please considering pledging us on Patreon

User avatar
Aaron
Posts: 2717
Joined: Sat Jan 03, 2015 4:03 pm
Location: St. Paul, MN

Re: Electrical wire crossing cold air return duct

Post by Aaron » Mon Oct 22, 2018 6:51 pm

You may have to use a fire-barrier type of sealer too, I think that's code in most places. It comes in expanding foam, caulk, and putty.

User avatar
Shannon
Posts: 11413
Joined: Fri Nov 25, 2011 11:58 pm
Location: Canada
Contact:

Re: Electrical wire crossing cold air return duct

Post by Shannon » Mon Oct 22, 2018 6:57 pm

Aaron wrote:
Mon Oct 22, 2018 6:51 pm
You may have to use a fire-barrier type of sealer too, I think that's code in most places. It comes in expanding foam, caulk, and putty.
I do not think in Canada it is But you are likely correct for the US. You guys are way more sticky on residential fire blocking. In any event it will not hurt anything to be on the safe side.
If you've found our videos or website information helpful, please considering pledging us on Patreon

User avatar
Aaron
Posts: 2717
Joined: Sat Jan 03, 2015 4:03 pm
Location: St. Paul, MN

Re: Electrical wire crossing cold air return duct

Post by Aaron » Tue Oct 23, 2018 1:40 pm

Shannon wrote:
Mon Oct 22, 2018 6:57 pm
I do not think in Canada it is But you are likely correct for the US. You guys are way more sticky on residential fire blocking. In any event it will not hurt anything to be on the safe side.
Yeah I know, it's because you're in a colder climate and fire is not as hot up there, remember? :lol:

User avatar
Shannon
Posts: 11413
Joined: Fri Nov 25, 2011 11:58 pm
Location: Canada
Contact:

Re: Electrical wire crossing cold air return duct

Post by Shannon » Tue Oct 23, 2018 2:14 pm

It’s so cold we hope for small fires! Lol
If you've found our videos or website information helpful, please considering pledging us on Patreon

rao.manoj2004
Posts: 19
Joined: Mon Oct 22, 2018 3:29 pm

Re: Electrical wire crossing cold air return duct

Post by rao.manoj2004 » Fri Oct 26, 2018 6:53 pm

Reply from 3 experts :)
Thanks a lot