Romex running along basement floor

Ask your electrical related questions here
Post Reply
badali
Posts: 30
Joined: Mon Dec 10, 2018 6:49 am

Romex running along basement floor

Post by badali » Thu Jan 17, 2019 9:49 am

Hi,

I've found some existing electrical which is parged in and running along the floor in the basement.
IMG_20190116_214807-01.jpeg
IMG_20190116_214807-01.jpeg (89.93 KiB) Viewed 130 times
This can't possibly be in line with building code right? Seems dangerous.

I am redoing the wall and am thinking of running the wire from above.

User avatar
Aaron
Posts: 3329
Joined: Sat Jan 03, 2015 4:03 pm
Location: St. Paul, MN

Re: Romex running along basement floor

Post by Aaron » Thu Jan 17, 2019 2:43 pm

No that's a pretty egregious code violation.

NM cable cannot be embedded in any material except for Type NMWU (Canada) or Type NM-UF (USA) which can be buried in earth (soil). It must otherwise be dry and secured with staples or holes in or through wood studs.

Absolutely follow through with your plan with running it from above; that's the way it should be correctly installed in a basement or garage. When it's not running through holes in wood (studs or joists), be sure it's properly secured at least every meter.

User avatar
emtnut
Posts: 1862
Joined: Mon Mar 02, 2015 7:21 am
Location: Canada
Contact:

Re: Romex running along basement floor

Post by emtnut » Fri Jan 18, 2019 11:40 am

:shock:

The concrete will eat away at that cable, Abandon it altogether !

It is definitely a code violation !
~~ Ford Ford Ford Ford Ford Ford :mrgreen: ~~